Testing of 33kV power cable
I want to perform the High voltage test for 33kV power cable.
1. what is max. applied voltage in case of AC supply as well as DC supply?
2. which standard i have to refer?
RE: Testing of 33kV power cable
If you are in Canada these standards may help:
CSA C68.3 Shielded and Concentric Neutral Power Cables Rated 5 - 46 kV
CSA C22.2 No. 0.3  Test Methods for Electrical Wires and Cables
Before you consider doing a DC hipot you should serch for threads here on that topic.
IEEE std 400.1 for dc
IEEE std 400.2 for VLF (very low frequency)
Also manufacturer recommendation are a good ressource as said before