breaking of coupling

breaking of coupling

breaking of coupling

(OP)
we are having 3 turbine generators & 3 diesel generators running in synchronisation. one of the turbine tripped. Due to failure of load shedding the complete bus collapsed.Also the coupling ( shear pin )broke. As per the manufacturer the shear pin is rated for 19 MW load. My total power drawn from the synchronised bus is only 9 mw.
can anybody guide me the reasons of failure so that it can be avoided. we could not find out any.

RE: breaking of coupling

I think that it could be very difficult to answer without a deep study.
This is a tipical phenomena that could be studied with a program for electromagnetic analisys. Some of the results are the mechanical and electrical torque during the transient. The steady state torque is less than the limit of the shear pin but the transient torque could be much higher.

RE: breaking of coupling

I think Alex had a good plausible answer.  When there is a transient, the machines angles and powers will swing, which certainly could be the cause.
 

RE: breaking of coupling

This is no more than some thoughts around what alex68 already stated...
when the turbine tripped, the whole rotating mass was deccelerating, if the generator breaker was still closed for some time (i.e. the gen breaker did not trip with the unit)you are actually feeding reverse power (motorizing) the generator.
If there was a spike in the motorizing power (an impact load) that could have caused the failure of the shear pin.
saludos.
a.

RE: breaking of coupling

Suggestion to smitanuj (Electrical) Aug 10, 2002 marked ///\\\
we are having 3 turbine generators & 3 diesel generators running in synchronisation. one of the turbine tripped.
///Do you have generator breakers?\\\
 Due to failure of load shedding the complete bus collapsed.
///What is the total Generating Capacity and what are individual generator ratings?\\\
Also the coupling ( shear pin )broke. As per the manufacturer the shear pin is rated for 19 MW load.
///What is the size of the Set?\\\
 My total power drawn from the synchronised bus is only 9 mw. can anybody guide me the reasons of failure so that it can be avoided. we could not find out any.
///Could you describe the power distribution system? Are all generators connected to one bus, or is there a ring bus?\\\

RE: breaking of coupling


Have you carefully reviewed the dimensional conditions of the shaft and coupling before restart?  It seems that scoring could be most undesirable, particularly at the stated power levels.
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources