Pump Mix for Concrete Wall Construction
Hi Guys
I have a case where the contractor would like to use a concrete pump to pour a 4m high wall in one go. The structure is water retaining (as per BS8007, the British Code for water retaining structures). I know that a pump mix is very different to a normal mix, it has a high slump, possibly plastisizers as well. I am no expert in the design of a typical pump mix, but my question is whether there are any problems that could occur when using a pump mix in walls (250mm thick wall). In my experience pumped concrete is generally used to construct slabs, not walls. Seeing that the wall needs to be water retaining, could there be issues with shrinkage cracking or any other potential problems stemming from the use of a pump mix?
Seb
Seb
RE: Pump Mix for Concrete Wall Construction
1. Keep the water/cement ratio low - 0.36 to 0.45
2. Plasticizers don't add to the w/c ratio
3. Use aggregates (coarse) that are 1 to 1 1/2" (25 to 40 mm) max. size. Don't use small aggregates without the larger sizes.
4. Here in the US - the ACI 350 requires a higher amount of horizontal reinforcement to control crack width. Don't know what standard you would design to but there should be an equivalent one.
5. Don't use higher strength concrete. Higher cement (richer) mixes shrink more.
6. ACI 350 also provides for control joints or expansion joints in walls at various distances and this spacing affects the required amount of horizontal reinforcement.
7. The wall pour sequence can be planned out ahead of time to minimize shrinkage affects on the walls...i.e. placing the corners last.
Do not allow the use of a "typical" pump mix with small aggregate. The strength will likely be higher, but the shrinkage will be relatively large.
If, perchance, the wall has only a single layer of reinforcing, then there should be no problem, considering an 8" minimum thickness of wall.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
Mike McCann
MMC Engineering
Motto: KISS
Mike McCann
MMC Engineering
Motto: KISS
While several factors affect choice of inside pump diameter, none is more important than the MSA.
In many areas 1-1/2 inch MSA mixes are not pumped but are "chuted". So it is not uncommon for a concrete pumping company (that is accustomed to pumping 1 and 3/4 inch mixes) to have problems when a 1-1/2 inch mix is ordered by the concrete contractor. Most are simply caught of guard, "Gee wiz (plus some other colorful vocabulary), we only have a 4-inch pump here to pump the mud!!!"
As a rule of thumb, the inside diameter of the pump and placing line should be 3 to 4 times the MSA. While a 4-inch diameter pump will work fine with a well proportioned 1-inch MSA mix, chances of it working with a 1-1/2 MSA mix are slimmer. A 6-inch diameter line should work fine with a 1-1/2inch mix.
I'm not sure this is entirely correct. The concrete design code which I use (Australian Standard AS3600-2009) gives smaller shrinkage strains for higher strength concretes. I can post a excerpt if you would like.
the BS Standard is 8007:1987, I think this will limit the crack width to 0.2mm.
I'm not sure about point 2. Plasticisers should help to keep the w/c ratio low while improving the workability of the concrete. But I believe all liquids, including plasticisers, are included in the calculation of w/c ratio.
As has been mentioned an important factor is finding enough space in the rebar to get the pump discharge low down inside the formwork
I just got off a project/study where a very rich mix added to the shrinkage - in this case it was autogenous shrinkage, not drying shrinkage alone. Rich mixes definitely can add to shrinkage problems.
What is the effect on the concrete of using too much plasticizer? Are there any negative effects?
BA
For a typical concrete mix, say with a water-cement ratio of 0.5, only about 50 to 60 percent of that water is required for hydration of the cement. The remainder is "water of convenience" or water to aid placement. While that remaining water is very important, it is also the water that partially evaporates from the concrete. As this water goes away, the resulting drying causes shrinkage.
The water used in the hydration reaction is a part of the autogenous shrinkage that JAE noted. Autogenous shrinkage is a result of the chemical reactions that take place during hydration and curing. In a simplistic manner, the resulting chemical compounds take up less space than the elements and compounds present before hydration. This shrinkage component is typically less than drying shrinkage, but does increase with richer mixes, simply because there is a greater volume of reactant (the cement).
hokie66 is right in that the "bulk" water is what causes most of the shrinkage, as just explained. As he also noted, the placement can be enhanced by reducing some of this water by using admixtures, with the side effect of increasing the strength because of the lower resulting water-cement ratio.
Mix designs are a somewhat delicate dance (concrete in a tu-tu?) of placement, performance and strength. Achieving all three is not usually done by accident!
As for the effect of too much plasticizer....the two most common problems are set times and segregation. The set time can be affected either up or down, depending on the admixture and the dwell time of the plasticizer can be a sudden shock during placement...I've seen concrete go from a high slump to stiff in a matter of minutes.
Ron: concrete in a tu-tu? You should be a writer - a flair for words and a lot of imagination!