Controllogix - Events

Controllogix - Events

Controllogix - Events

(OP)
anyone with any info?

trying to add a digital input Change of State event to my program. Have created the task, the program and a simple routine which increments a dINT, to confirm the call. Event set up as COS, tagged to an AC input module. That module then has a single input set for COS on rise.

Problem is the incrementing dINT indicates continous call regardless of input status. Monitoring the task shows it's called every 20ms, same as the RPI rate. The module does reside on a remote rack over DeviceNet.

I'm stumped.

RE: Controllogix - Events

(OP)
correction, running over ControlNet

RE: Controllogix - Events

Do you have this input checked only on this card for either ON>OFF or OFF>ON input change of state?
Cant have other IO points checked besides the above input on this card or these will affect the event.

Under the task config, do you have it set for the following:
Trigger = Module Input Data State change
Tag =  the Input data IO point

Remember if the event is over controlnet there is the NUT delay added to this input response.  Versus if it was in the local chassis where there is only a RPI delay of .2mSec

RE: Controllogix - Events

(OP)
Thanks for that. Every thing set as you've indicated. I was able to resolve the problem my switching to a module in the local chassis. In reading docs, it appears that the event will fire on the reciept of packet from remote chassis, where as in the local chassis, an COS can fire the event seperately.  

RE: Controllogix - Events

thought this pdf was helpful on events
1756-rm094_-en-p
Logix5000 Controllers Design Considerations
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources