Question: What would be the appropriate type of natural gas detection system for a natural gas fueled industrial oven in a large warehouse/forging facility? Is there a specific type of detection system, spacing, etc? The model codes do not require a detection system, however, the owner has voluntarily installed a system.
I have attached a cut sheet for the proposed type of detection device.
Thank you in advance.
I have attached a cut sheet for the proposed type of detection device.
Thank you in advance.





RE: Natural Gas Detection
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
Chinese prisoner wins Nobel Peace Prize
RE: Natural Gas Detection
Good piping practice ensures that gas piping doesn't leak. And the mercaptan in the gas is there so humans smell it and make a stink about it so the leak is fixed.
Flame safety sensor/control ensures that the oven's fuel supply is shutdown within second of loss-of-flame detection. This is not new, untested 'technology', it's decades old standard design practice.
If the flame safety is up to snuff, there isn't real reason to be concerned.
There are plants with dozens of gas fired furnaces/ovens/kilns that have no independent gas detection sensor/alarms that I go into where I have zero concerns about safety.
What's the root fear that stand-alone gas detection is needed? Where's the gas going to come from?
If this company wants to blow money, the conventional sensor is a combustible gas (methane) LEL (lower explosive limit) sensor.
RE: Natural Gas Detection
Because of its toxicity, detecting CO makes more sense than detecting methane for a commercially designed (code compliant) oven/furnace.