Where can O find a Dummies guide to G59 testing ?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: G59 TESTING
RE: G59 TESTING
Ground dectection overvoltage relay?
Overvoltage relay connected across broken delta windings of grounded-wye / broken delta grounding transformer?
Neutral-ground overvoltage relay on generator or transformer grounding resistor?
RE: G59 TESTING
If you really are a dummy then find an experienced commissioning engineer to do it as the local distribution Company may well want to witness the testing, and it won't instill much confidence if you don't know what you are doing.
ps a tip for the future. Use of the word "please" may well illicit a more helpful response.
Regards
Marmite
RE: G59 TESTING
It's a Guidance Note issued by the UK's Electricity Association which deals with the need to disconnect small embedded generation from the system in the event of system collapse. It is typically implemented using one or both of df/dt or vector shift. Setting these relays is highly depenedent on the machine itself and the local system conditions.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: G59 TESTING
RE: G59 TESTING
----------------------------------
If we learn from our mistakes I'm getting a great education!