Room design method - attic

Room design method - attic

Room design method - attic

(OP)

As a combustible attic space frequently governs the water demand requirements,the cost of water storage and pump capacity can be lessened by having the /architect contractor separate the attic into 30min. rated compartments with self-closing access hatches between compartments which would satisfy the requirements for room design method.

Any thoughts/concerns?

Thanks

R M Arsenault Engineering Inc.
www.rmae.ca

RE: Room design method - attic

I have seen these fire partitions in many apartment complex.  The main problem is that these hatches are left open so it may be best to eliminate them.

RE: Room design method - attic

(OP)
I agree.  The hatches are my concern too.

R M Arsenault Engineering Inc.
www.rmae.ca

RE: Room design method - attic

Not a designer or engineer

Does 13 back this design in an attic???

And we are talking commercial not residental ?????

RE: Room design method - attic

(OP)
This is an assembly occupancy so commercial.   The main criteria for use of the room design method is the requirement to calculate the demand of a room that has a fire separation that is equal to the required water demand duration. An attic is a light hazard combustible concealed space.  If the attic was occupied, you could divide into 30min fire separated rooms and use the room design method.  So I see no reason why if it is unoccupied you couldn't divide it the same way and use the room design method.  NFPA 13 doesn't explicitly define what a 'room' is.

R M Arsenault Engineering Inc.
www.rmae.ca

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources