Transformer MCB

Transformer MCB

Transformer MCB

(OP)
In my control panel, I have a type B 16Amp MCB for a 240v-110v transformer.

Every time when I started the panel, the MCB always tripped. Not only that, it also tripped the mains' MCB. (I didn't design the panel)

Later on I learned that a D type MCB is more suitable for a transformer.

Once the control panel is up and running, it seems to work fine and the MCB doesn't trip.

So I'm just wondering if I can get away with leaving the MCB I have already got in there or do I have to replace it with a type D?

Thanks
 

RE: Transformer MCB

I would try to use a C curve MCB where possible, rather than a D curve. Most E-I type transformers will be ok on a type C, although toroidal types almost always require a D because of the very high inrush. D curve breakers can be awkward to coordinate with upstream protection unless there is a big size ratio between them.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Transformer MCB

ScottyUK,
I would think that if the Main is occasionally tripping, it would indicate that his inrush may already be exceeding what a C curve will hold at, no?

"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: Transformer MCB

jraef,

There are lot of B curve MCBs in the UK - seems to be the default offering by most manufacturers. I tend to use a C curve as default for a circuits feeding sockets, but it's by no means a standard. It's not that hard to trip a 32A type B MCB by plugging in a portable tool transformer or similar.

It would help to know what type of transformer, and what size, was involved, then we wouldn't have to guess!
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Transformer MCB

(OP)
Thanks all

3 KvA Transformer 240v-110v, does this help?

RE: Transformer MCB

Yeah, that's pretty big for a 16A breaker. I'd be tempted to protect it with a 20A type C breaker - size the wiring appropriately - and use an MCB on the secondary side for transformer overcurrent protection.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources