Timber Floor Panel/Joist Connection
I hav'nt done much work with timber before and I need to deermine the size and amount of screws I need to connect OSB flooring to a sold timber joist. I not quite sure how to go about it. Is it governed by shear forces?how would you consider the connection to be loaded?Please Help......Thanks!
RE: Timber Floor Panel/Joist Connection
I believe this is to do with diaphragm action and preventing bcuckling of the board, it is not for bending strength.
As csd said design it for shear as you would any other diaphragm, assuming you are using it as one. I recommend screws and glue to prevent squeaks and noises which is the #1 complaint when it comes to homeowners and wood floors...
Design for shear. A standard screw should give you a nominal shear capacity of 1 or 2kN. I would fixings every 12" with elastomeric adhesive. If this can transfer the shear forces from the diaphram to the bracing element than I would leave it at that.
The minimum floor diaphragm for nails is 6" at the plywood or OSB panel edges and 10" OC in the panel field.
I would use the same for screws, making sure the shear capacity of the screw was the same as the IBC table shows for nails.
Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask