Sizing Open Vents

Sizing Open Vents

Sizing Open Vents

(OP)
How do you go about calculating the maximum air flow through an open vent on a storage tank assuming it is a swan neck breather (so 2 elbows and 200mm of pipe) when the tank is discharging and filling?

I have heard that you should carry out a pressure loss calculation but I do not know where to start.

For arguments sake how would I find what size swan neck breather to install on a tank venting at 200m3/hr?

Thanks

RE: Sizing Open Vents

For petroleum storage, API-2000 requires that conventional vents be flow-tested.

The ASHRAE handbooks have some duct-flow and fitting-loss information that can be applied otherwise.

RE: Sizing Open Vents

The calculation is really trial & error.
The first step is to determine the tank's pressure and vacuum rating.
Second step is to assume a pipe diameter.
As an example, if the pressure rating is 10" h20 and assume 2" pipe.
The friction loss through the 2" swan neck would need to be less than 10" h20 at 200m3/hr flow.
If the fricion loss is too high, redo the calculation for larger pipe.
Similar logic for the vacuum side.

JStephens is correct -- use a calibtaed device if you need to follow API-2000 standards.
Years ago, Groth used to sell calibrated Swan neck vents
but today I do not know where to purchase similar hardware.
Otherwise Note that OSHA requires a 100% safety factor be applied for uncalibrated venting devices.
So the calculation would need to be at 400m3/hr flow to satisfy OSHA.
Additionally, most swan necks I have seen have bug screens which typically reduce the flow area to 2/3 of base pipe area.
I typically add one pipe diameter if a bug screen is used.

Normal filling and pumpout is typically small flows compared to other ways to overpressure a tank.
Consider also nitrogen pad requlator failure.
Consider also the maintenance practice of clearing connecting pipe by air blowing.
A 3/4" air hose 10-ft long with wide open block valve can generate alot of pressure which must be vented.
 

RE: Sizing Open Vents

Also consider icing up of the bug screen if you are in a cold climate.  Using 3/4" mesh screen should help this while still excluding birds.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources