velocity criteria for PSV suction line
Dear All,
 there is any guideline regarding velocity criteria for PSV suction .
thanks in advance
RE: velocity criteria for PSV suction line
You mean the inlet line to the PSV, right?
Good luck,
Latexman
right sir, there is any guideline regarding velocity criteria for  inlet PSV line. Some where i read that 70% of sonic velocity can treat as for same. can i take this for all time ?
please help me.
thanks in advance
No, there is just the "3%" rule, see API 520. 70% of sonic is way too high.
Cheers,
Joerd
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.
I would agree with joerd. There is just the "3%" rule for the grass root design as per API guideline. Although I have seen engineers take slightly higher pressure drop acceptabe in older/existing facilities.
So when you design for 3% od set pressure of PSV as pressure drop (inlet line)the velocity you get is the acceptable velocity.