Published transformer X/R ratios

Published transformer X/R ratios

Published transformer X/R ratios

(OP)
Does anyone know where I can find published X/R ratios for transformer especially those in the kVA range?  I looked in the IEEE Red Book and I only see a table for X/R ratios for transformers in the 1MVA range and higher and I was wondering if there was another reference that I am missing?

RE: Published transformer X/R ratios

(OP)
dpc

Thanks for the tables they are helpful!

Where does SKM reference its R and X values from?  For a 75kVA dry type transformer I cannot seem to match the values given to any one of the attached tables?

RE: Published transformer X/R ratios

(OP)
SKM gives a X/R ratio of about .875 for this 75kVA transformer.  This seems lower then the above publisehd information.

Isn't there an IEEE standard for transformers that would give all of these typical X/R values?

RE: Published transformer X/R ratios

Quote:

SKM gives a X/R ratio of about .875 for this 75kVA transformer.  This seems lower then the above publisehd information.
The X/R given in David's GE reference for a "QHT" 75 kVA dry type transformer (p.34) is 0.841.  Cuky's graph shows a 75 kVA dry type data point with an X/R between 0.5 and 1.  Seems like pretty good agreement to me.

RE: Published transformer X/R ratios

For SC calcs. , the X/R range of the published values provide acceptable results for most practical purposes.

If you are doing any special application, that require high level of accuracy, I suggest to obtain the actual data of the specific transformer and work with the manufactor and test lab.


 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources