feed 2 loads from transformers
feed 2 loads from transformers
(OP)
I am trying to tap an additional load from a particular transformer. My co-worker told me he has done that before and that should work but I just want to have more opinions.
This transformer currently feeds an MCCs (2 sets of 4-350kcmil). I want to tap its bushing to feed a panel that will feed motors (combination starters) and of course I will protect the panel with a breaker. This transformer has enough to feed both de MCC and the panel I will use.
My question is : can you feed 2 differents circuits from same transformer if there are bushing spares?
Thank you guys
This transformer currently feeds an MCCs (2 sets of 4-350kcmil). I want to tap its bushing to feed a panel that will feed motors (combination starters) and of course I will protect the panel with a breaker. This transformer has enough to feed both de MCC and the panel I will use.
My question is : can you feed 2 differents circuits from same transformer if there are bushing spares?
Thank you guys






RE: feed 2 loads from transformers
RE: feed 2 loads from transformers
As for more options, I always try not to saw seeds for a mess to grow. I would put a distribution board.
Rafiq Bulsara
http://www.srengineersct.com
RE: feed 2 loads from transformers
Rbulsara, putting a distribution board is a good option. but we want to see if we could connect our load straight into the secondary of the transformer then connect it to a panel board for the new load.
This is mainly because it will cost us lots of money if we were to remove the actual wiring and connect it to a panel distribution...
RE: feed 2 loads from transformers
How will a fault or overload on your new feeders be cleared?
Bill
--------------------