i will be doing a small 2-story structure with pre-cast walls. pre-cast wall done by others.
what information do you normally supply to them if pre-cast wall is not your scope?
what information do you normally supply to them if pre-cast wall is not your scope?






RE: pre-cast wall done by others
thanks,
RE: pre-cast wall done by others
If this wall is a fire wall then it will need to have minimum thickness for fire rating, the precaster will not know this.
RE: pre-cast wall done by others
it may not be the case in my structure coz i am looking at a similar structure drawing as go-by, it just say 7" thk reinforced conc. insulated panel.
didnt specify the how many rebars so am guessing it should have been designed by others.
even embedded plate is by panel mfr.
RE: pre-cast wall done by others
RE: pre-cast wall done by others
You will need to provide a full set of loads to the manufacturer.
RE: pre-cast wall done by others
RE: pre-cast wall done by others
1. Typical panel section.
2. Typcial panel connections (base, mid height, and roof). If your panels are connecting to any flexible beams you might want to use a connector that will allow the beam to deflect freely.
3. Basic design loads.
4. Site Class so they can figure out the minimum seismic loads if these are non-load bearing.
It is up to the precast designer to figure out the rebar requirements, lifting arrangements and all the other specifics. I wouldn't waste your time trying to figure out this out because each precaster has their own preferences when it comes to panel sizes, lifting hardware, and manufacturing. Whenever consultants have tried to do so for my clients projects, they get it all wrong and it usually ends up in more discussions than necessary.
Brad