Mechanical Room open to the return plenum?

Mechanical Room open to the return plenum?

Mechanical Room open to the return plenum?

(OP)
I am working on a project, and there is a 20-ton air handling unit and electrical PDU (about 4kw heating load) in the mechanical room. The wall of the mechanical room doesn't go all the way up to the structure, and open to the plenum space above the ceiling. All the plenum return air in other areas will return to the back of the air handling unit in the mechanical room. My question is: Do I need to supply some cooling air in the mechanical room? If not, how do I estimate the return air temperature rise because of the heat from the electrical PDU?
Thanks for advice.

RE: Mechanical Room open to the return plenum?

sfxf:

Don't supply cooling air into a mechanical room acting as a return plenum! There is plenty of cooling air from the return volume passing through the space.

I estimate this is an ~8,000 cfm unit based on a rough thumbrule of 400 cfm per ton. Also based on a standard (estimated) 20% outside air, your return volume might be 6,400 cfm. Using the formula:

Q = 1.08 * V * dT, where

Q = heat gain in BTU/Hr,
V = flow in cubic feet per minute (cfm), and
dT is the temperature rise (°F) from sensible heat,

and the Q is given as heat output of 4 KW (13,652 BTU/Hr), the 1.08 a conversion, and the cfm of return air passing through the space an estimated 6,400 BTU/Hr,

I would predict a 2°F temperature rise in the return air. Rough. Subject to factors that help make HVAC an inexact science; subject to ACTUAL heat output, not manufacturer-stated output, of the PDU (note that often a typical operating heat output of an electric piece of equipment might be 15-30% of the manufacturer-stated design heat output, which might bring us down to a half a degree or so).

There's no need to condition this mechanical room with its current air exchange rate. Let the return draw past the panel and accept that there may be a 2°F temperature rise from the return plenum to the AHU mixing chamber. This just means that the AHU will have to work a little harder to do its job in cooling mode. And it means that it will need to work less hard to heat the air during the winter and will allow you to take in more fresh air for ventilating.

If there is a temperature economizer cycle, make sure the return air sensor is inside the unit intake and not in the plenum or mechanical space.

Best of luck, -CB

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources