Motor Failure under single phasing
Motor Failure under single phasing
(OP)
A star connected induction motor, 2.2 kW 400 V 3 phase supply, integrally connected to an oil pump,failed with over current.Oil is circulating through the stator of winding,therby getting cooling.
Instead of a no -load current of 1.8-2.2 A, motor took 3.6,1.8 and 5.52 A current in three lines.Full load current 5 A and the motor is protected by a 6A MCB.
On inspection, stator overhang area is burnt.What can be the probable cause of failure? Vendor says it is due to single phasing and overvoltage of 2.5 kV might have come which caused sparking from stator to ground.Difficult to accept that loss of a phase can cause such failure.Can the experts explain the probable failure mode?
Instead of a no -load current of 1.8-2.2 A, motor took 3.6,1.8 and 5.52 A current in three lines.Full load current 5 A and the motor is protected by a 6A MCB.
On inspection, stator overhang area is burnt.What can be the probable cause of failure? Vendor says it is due to single phasing and overvoltage of 2.5 kV might have come which caused sparking from stator to ground.Difficult to accept that loss of a phase can cause such failure.Can the experts explain the probable failure mode?






RE: Motor Failure under single phasing
Why isn't the motor protected by a thermal overload relay? MCBs are a poor match for a motor damage curve, which is one reason why they aren't normally used for this duty.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Motor Failure under single phasing
RE: Motor Failure under single phasing
It's true that unbalanced voltage poses some unique challenges for rotor due to high frequency and skin effect of the reverse rotating field. That produces heat in the rotor which can also end up raising stator temperature. Additionally, the unbalanced voltage produces negative torque which must be overcome by additional positive torque, so the motor draws more stator current to drive the same load. The rotor tends to be a lot more beefier and it's not surprising to me that the stator gets overheated and not the rotor.
MCC-fed motors typically include a combination starter with thermal overload protection. I have seen the transformer fans and pumps are usually not fed by an MCC and instead simply protected by long-time protection built into the breaker in the control cabinet, which as Scotty mentioned will not be as closely matched. Unbalance and open-phase is tricky to protect against to begin with since the amount of heating (including rotor effects) may not be truly reflected in stator current magnitude.
=====================================
(2B)+(2B)' ?
RE: Motor Failure under single phasing
htt
http://www
Hopefully you can see what I mean that single phasing can be evident from the endwinding.
Of course single-phasing can be an initator outside the motor from the power system, or it can be result of motor internal failure. You mentioned spike to 2.5kv...not sure how that fits in but certainly can be the beginning of many types of failures.
I think it would be tough for anyone here to judge the failure cause without a lot more info: pictures, test results, conditions at time of failure, power system grounding, etc. I would tend to trust the people that looked at the winding (assuming they were provided sufficient info about the failure) unless you had other evidence to contradict what they said. But certainly doesn't hurt to talk about it and more info will give better responses.
=====================================
(2B)+(2B)' ?
RE: Motor Failure under single phasing
I'll guess this is an OFAF or ODAF transformer, and that the pump is energised as a second or third cooling means after the transformer operates in ONAN and ONAF modes at lower temperatures. Presumably the motor is switched by a contactor, in which case it would be a trivial exercise to add a standard thermal overload relay. Most transformer pumps would be quite happy with a Class 10 overload because they run up to full speed quickly. Upstream of the contactor would typically either be a breaker or a fuse, providing short-circuit protection in addition to protecting the wiring within the compartment against overload.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Motor Failure under single phasing
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Motor Failure under single phasing
RE: Motor Failure under single phasing
There are two failure modes.
On single phase, the motor has about 1/3 the torque. As a result it slows down a little. But when it slows down, it slides down the torque:current curve. One phase must now supply enough current to develop the torque to drive the load. If the load is much more than 1/3 of full load, the energized winding may fail.
This failure mode occurs when the phase lost is limited to the motor circuit.
If an incoming phase is lost and the motor is connected to a panel with other non-motor loads, then the motor acts as an induction generator and attempts to supply the loads on the missing phase. If "B" phase is lost, you will be supplying loads on both "A-B" and "B-C". So expect the backfeed current on the motor "A" phase to be about the sum of the backfed currents on "A" and "C".
This failure mode may cause motor failure even with no mechanical load on the motor.
This effect may be useful if the current is within the thermal capacity of the motor.
That's how a rotary phase converter works.