Earthquake - ground motion amplification in fill
1)Is there a fundamental difference between how seismic waves amplify through an engineered fill vs. an in-situ soil profile? i.e. 30 feet of engineered fill on bedrock vs. 30 feet of alluvium (assume similar soils).
2)If you have an engineered fill 30' thick over bedrock, does that impact design of the structure when compared to a natural deposit (again ... assuming similar soils) - from the soils end? Seems like a Site Class D is a Site Class D regardless of how you get there (but perhaps my ignorance for question 1 is showing).
I have a site that is being scrutinized because we have 30 feet of fill, whereas, if we had 30 feet of alluvium no one would care - we'd just proceed with Code ... and I'm confused (or the other guy is :D). I understand that a fill would potentially respond differently, i.e. maybe the associated strains are greater, but I'm having a tough time envisioning that in 30 feet we could get a substantial difference in wave motion when comparing a fill to alluvium (again ... assuming the soil properties are similar).
RE: Earthquake - ground motion amplification in fill
with that said, what type of soil is important as various soil types will amplify the base rock motion. Hence you will always see a soil factor equal to or greater than 1.0.
2. With engineered fill you can improve the site classification and or densify the soil to provide the same effect of the structure on bedrock as on soil.
I hope this helps. Engineered fill is good pending on what type of soil and compaction. It will generally perform better than insitu soil.
![[pipe] pipe](https://www.tipmaster.com/images/pipe.gif)
Qshake
Eng-Tips Forums:Real Solutions for Real Problems Really Quick.
Dik
In concept, the principle should be the same as in natural soils, but, as Qshake points out, compacted engineered fill may have different elastic properties. The consequent seismic soil calss could even be more favourable than an alluvium soil.
If you have a technically sound counterpart, you may reason that the input parameters for amplification are Vs, density, G (shear modulus) degradation curves and D (damping) degradation curves.
If it can be reasonably shown that such fill parameters are not more unfavourable than your average 'alluvium soil', than they should be all right.
I plotted up the spectral response curve for each Site Class C, D, and E(ultimately a lesson in futility, but it made my nerdiness feel complete). From there I compared the equivalent base shear and simplified base shear (ASCE 7-05) for the varying site classes (that was easy since the only thing that changes is Sds when the structure is constant). Essentially what I got out of this process was that for a short period structure, there's very little difference in seismic loads when varying between site class C, D, or E. Which is bolstered by the fact that when you run through Code ... all three lead you to a seismic design category D2. So it seems to me, that until your structure gets taller, longer, more complicated... worrying about seismic amplification (except for Site Class F) and its effects are kind of overrated??? Please feel free to refer me to Earthquakes for Idiots ...
I have gone through the same exercise as you , and often it will not matter, but that is no reason to provide incorrect information.
My question is ... if everything circles back to a D2, is the structural design impacted by whether or not the Site Class is C, D, or E. It appears to me it is not. If it is ... where/how is that impact manifested?
Hey Moe. Thanks; yes, I've seen how variation in location can impact design catergory. The scenario I've presented seems kind of hinky in that I can have a Site Class c thru E and it doesnt impact the design??? I'm trying to make sure I haven't missed something.