(OP)
I was wondering about Covered patios. I have been looking into the requirements about when they are required. I hear this both ways about when they are or are not required, and I can't find anything in NFPA 13. Am I just missing it?

RE: Covered Patio

Do not have the book with me

Look under canopy or overhang

Normaly anything over 4 feet with some exceptions

RE: Covered Patio

Take a look at NFPA 13 2010 8.15.7, beginning to end.  Should answer all your questions.

RE: Covered Patio

If you are dealing with Group R-2 apartments of combustible construction, the 2009 International Fire Code has sprinkler protection requirements that are more restrictive than NFPA 13 for balconies and decks.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources