I'm sorry if this comes across as too basic to ask but here goes.
Need to calculate the Full Load Amps on the primary side of a 480V-120/240V, single phase transformer being supplied by only two ungrounded conductors from a three phase system. I'm told that the FLA is the kVA/480 because the load is single phase. I thought the FLA should be kVA/(1.732x480) because the system that "sees" the load is still a three phase system with the phases 120 degrees apart? How do you calculate a "two" phase load on a three phase system?
Need to calculate the Full Load Amps on the primary side of a 480V-120/240V, single phase transformer being supplied by only two ungrounded conductors from a three phase system. I'm told that the FLA is the kVA/480 because the load is single phase. I thought the FLA should be kVA/(1.732x480) because the system that "sees" the load is still a three phase system with the phases 120 degrees apart? How do you calculate a "two" phase load on a three phase system?






RE: Protection of Transformer Primary
Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.
RE: Protection of Transformer Primary
See last couple of posts in thread238-261481: 3 Phase Power Monitor.
Rafiq Bulsara
http://www.srengineersct.com
RE: Protection of Transformer Primary
RE: Protection of Transformer Primary
A = kVA/kV
RE: Protection of Transformer Primary
Rafiq Bulsara
http://www.srengineersct.com
RE: Protection of Transformer Primary
Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.