Taps
Taps
I was ref 240.21 in the NEC on tap conductors I know its legal to make taps. My question can I tap off some #500mcm feeders with a #8 to the primary side of a XFMR which has OCP for the primary.
RE: Taps
Length of the tap conductors, which you did not mention, is a determining factor as well as tap conductor ampacity rating as a percentage of the tapped circuit rating.  Delve a little deeper into the NEC and I expect you will find your answer, but #8 tapped to 500 MCM sounds pretty small to me......and if it is short, why not go with bigger wire?
Alan
RE: Taps
racobb has your answer -- I'll go one step further. If under 10 feet and field-installed, you have a "maybe" situation, since the ampacity of the tap conductors must be at least 1/10 of the upstream overcurrent protective device setting (not the ampacity of the feeder conductors) per 240.21(B)(1)(4).  Also, the overcurrent device protecting the feeder conductors cannot take advantage of the "next higher standard size" exception.
Read 240.21(B) and all of its sub-paragraphs thoroughly.
If you want more of answer, give us a wiring diagram and distances.
Good on ya,
Goober Dave