(OP)
Please advise if there are any specific guidelines for bracing/supports for 480V 50kA Switchgear.  There seams to be a table/chart available from UL891 Supplement B for Switchboards but haven't come across anything for Switchgear.
Also, have not been able to actually "find" the Supplement B that many refer to, even when searching on the UL web site.  They only list Supplement A???

RE: Bus Bracing for Low Voltage Switchgear

Thats because Switchgear is designed, assembled, and tested in compliance with ANSI/IEEE standards in US. Try IEEE C37.20.1.  

"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic — and this we know it is, for certain — then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". – Nikola Tesla
 

RE: Bus Bracing for Low Voltage Switchgear

Also check UL 1558, which applies to LV switchgear. UL891 is for switchboards.

Rafiq Bulsara
http://www.srengineersct.com

RE: Bus Bracing for Low Voltage Switchgear

(OP)
Thank you both for your responses.
Yes, 891 is for Switchboards and 1558 is for Switchgear Assemblies.
It appears that UL provide charts (in Supplement B that I can't find on the UL web site)for mfgr's to build switchboards but to build swgr, one has to follow testing guidelines to prove it can withstand the levels it maybe subjected to. Therefore, there are no charts for swgr bus supports and bracing. If someone has a different information on this, please advise.
I know that there are companies out there that will modify existing bus systems for a higher IC rating and I wonder what they use for guidelines/calculations to warrant what they do.

RE: Bus Bracing for Low Voltage Switchgear

Re UL 891: There is no more Suppliment B.
    See Annex G (at the very end of the 891 file). Annex G covers 4000A maximum & up to 100,000 RMS.

1558 Switchgear: Supports & bracing must be per individual testing. Once that testing has been done, we can design per the spacings in our UL File.

RE: Bus Bracing for Low Voltage Switchgear

Powell Switchgear used to publish a set of technical papers, one of which described this issue and why there is no "standard". I had to wave that in the face of an over zealous nspector once. He still rejected it and siad I had to bring UL out to the jobsite to inspect it, assuming it would fail. I had to pay for a UL field inspection, during which the UL inspector came out and told him "It's fine, they tested it. THAT'S the standard." I was vindicated, I still had to pay the bill...

"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: Bus Bracing for Low Voltage Switchgear

Is that typical in the US - inspectors whose authority is out of balance with their knowledge, not adequately knowing the standards they are supposed to enforce and landing the customer with a bill because of their error? I'm surprised there isn't any recourse in such a case.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Bus Bracing for Low Voltage Switchgear

Yes Scotty, it is VERY normal. I work for a manufacturer and you'd be surprised at how many of our customers get conflicting data. One you might love. Requirements for ground fault testing on initial installation of service entrances. It IS required in many cases, though easily over half of the inspectors are unfamiliar with this rule.

Barry, the company I work for utilizes a arc-flash study along with a design program. The placement is dependant upon final kA rating.

RE: Bus Bracing for Low Voltage Switchgear

An extension of old axiom popular in such situations:

"Those who can't do, teach  But those who can't teach, inspect!"

Inspectors here are referred to as an "AHJ", Authority Having Jurisdiction. It means the are the demigod of their own little world. There is an appeal process, but you are loathe to use it if you are not prepared to be challenged on everything. Most inspectors are retired (or failed) contractors, not engineers. This one was a retired engineer, but he was not an EE, I think he was an ME, maybe even a CE.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources