Does anybody know a European manufacturer that makes cables for hazardous locations (Zone 1 and 21)?

I was looking at the webasitre of LAPP cables but they don't have cables for zones 1 and 21.
 

RE: European Cables for Hazardous Location

I'm not that familiar with European hazardous locations requirements, do you know what cable types are allowed?

For example in the US Type MC is allowed in Class 1, Div 2 locations but this isn't spelled out on every datasheet.  It's possible Lapp has some cables that are allowed but aren't described as such.  

I would look at Nexans and Prysmian as well.

RE: European Cables for Hazardous Location

(OP)
Thanks EricAXEWC, the Nexens cables are impressive. The cable at the following link is for onshore oil and gas facility, so it must be good for hazardous zones 1 & 2.

https://www.nexans.com/eservice/France-en/navigateproduct_540122992/IEC_60502_1_Unarmoured_4_x_185.html

But I am superseded they have not mentioned in the specification that this cable is good for hazardous zones 1 and 21.

Is it normal in European cables that they don't mention in the specifications that the cable is suitable for hazardous zones 1 and 21?

RE: European Cables for Hazardous Location

Allied to the correct gland, many common industrial cables are suitable for zones 1 and 21. The key factor may be the choice of a compression gland or a barrier gland.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: European Cables for Hazardous Location

Typically I would expect a manufacturer to list it to assist customers like yourself who are specifically looking for cable for hazardous environments.  But specs are specs, some are better than others.

Attached is a document that discusses cable gland requirements in hazardous locations.  It references European standards (EN) and their British (BS) counterparts.

I recommend looking at the country specific requirements you will need to meet, as always the AHJ has the final say on what is allowed / not allowed.

RE: European Cables for Hazardous Location

BS5308 - standard instrument cable
BS5467 - standard power cable, steel wire armoured
BS6116 - obsolete, elastomer-insulated cable
BS6346 - standard power cable, PVC insulated so not so common these days
BS6724 - standard LSF power cable
BS6883 - offshore elastomer-insulated cable
BS7917 - offshore elastomer-insulated cable

I didn't recognise the last two types at all, but the others are standard cables which may be used in a hazardous area when correctly glanded. I doubt you will find a BS cable specifically qualified for a hazardous area duty, other than for mining, but that industry comes under its own set of rules and regulations anyway.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: European Cables for Hazardous Location

See IEC60079-14 Electrical apparatus for explosive gas atmospheres — Part 14: Electrical installations in
hazardous areas (other than mines) Section 9 Wiring systems

Usually the cables are not certified for hazardous areas, it is up to the designer to select cables that comply with the requirements of IEC60079-14

As noted above the most important thing is to select the correct cable gland. You will find some pretty good info on this site http://www.ehawke.com/index.html

RE: European Cables for Hazardous Location

(OP)
Most European cable manufacturers make industrial power cables suitable for Class-2 Stranding (http://en.wikipedia.org/wiki/IEC_60228)

However I see that LAPP makes Class-5 power cables.

In my opinion it might be totally unnecessary to use Class-5 cables for industrial motor applications.

Please comment.

RE: European Cables for Hazardous Location

'Might' is the correct word. Depends totally on the application, which so far we don't know.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: European Cables for Hazardous Location

I agree with Scotty. See:
http://www.exindustries.com/prod_cables.htm
But I'd prefer MC-HL cable for exposed hazardous location or use of suitable conduit and accessories as per NEC art.500...
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources