UL508 Disconnect vs UL98 Disconnect
When is it OK to use a UL508 Disconnect in place of a UL98 disconnect on a UL508A listed panel?  We have a panel that mainly controls a motor, but has other circuits (ie. PLC, I/O).  This must go through UL certification soon.  I have heard multiple explanations on this and could use a NEC 409 reference or UL508A.  The panel, nor the equipment it controls, is not classified as "Industrial Machinery".
RE: UL508 Disconnect vs UL98 Disconnect
If your switch is required to be suitable as a motor disconnect or manual motor controller, it needs to be marked as such -- and UL 508 applies. (UL 508A 30.1.5 and table SA-1).
If not required to be suitable as a motor disconnect or manual motor controller, it can be UL 98.  (UL 508A 30.1.4 and table SA-1).
Those are my opinions; the opinions of your UL field inspector may vary.  Best suggestion:  ask him.
Good on ya,
Goober Dave