Cables-3C and 3-1C

Cables-3C and 3-1C

Cables-3C and 3-1C

(OP)
I have an application that I need to feed a 5MVA-27.6 Kv transformer through a switch. I can use a 3 X 1C cable or a 3C cable . I believe code has installation restrictions for non-armoured cables to be either inside a conduit or inside an enclosed cable trays.

Beside bending issue that we might have with triplex cables , what are other major concerns to consider when picking between triplex and 3 X 1C cables?
 

RE: Cables-3C and 3-1C

Purchase cost.
Installed cost.
Special treatment for three conductors to address sheath currents and eddy currents in enclosure iron.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Cables-3C and 3-1C

(OP)
We usually bundle all three sheath wires and ground it at the switch location. Will bundling three concentric neutrals and ground it have the same effect as if you have one concentric wire for 3C cable and ground it?

 

RE: Cables-3C and 3-1C

The three high voltage conudctors inside a 3-C cable will each have a concentric shield.  The overall jacket may or may not have a metallic shield, depending on the design.  If it is an armored cable, the armor makes on overall shield that needs to be grounded.

If you run three single-conductor armored cables and ground the three armor terminations at each end  it will create circulating currents.

Three conductor armored cables should not create circulating currents.

RE: Cables-3C and 3-1C

(OP)
In existing installation, bare copper wire shield is  grounded at both sides ( Switch and transformer). There are no LA used at each sides and distance between transformer and the SWGR is below 100'.

So if we replace the existing 3-1C cables with a 3C cables (as per attached) then we need to ground the " Tape Shield (E)" at both locations right? considering the short distance, I assume the cirulting wire is not an issue.
 "Ground Conductor (G)" acts as a bonding conductor.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources