Multi-battery design
Hi
I need to load banks of batteries OPZS (850 Ah c100) with one diesel generator of 60 kW.
The time of load foreseen is 6 hours a day.
Can someone recommend to me the most suitable system of load?
RE: Multi-battery design
Keith Cress
Thank you
Perhaps you need to spend a few more characters and explain in detail your problem.
TTFN
Chinese prisoner wins Nobel Peace Prize
The problem is that it is a lot of power the generated one. We would need banks of batteries and a suitable system of load.
This it is the problem.
I do not know if the problem is understood well
And, being able to withdraw the stored power at a later time?
TTFN
http://todoproductividad.blogspot.com/
What voltage is your generator?
Offhand, you're looking at something like 100 batteries for a 30kW*6hr excess capacity, assuming an 90% efficient charger.
TTFN
- 2V batteries OPZTS.
While not specifically suitable, a UPS has the architecture that you desire:
http
http://p
Just bear in mind that a UPS is typically specified for 10 minutes of operation at full capacity, so you'd still need the equivalent of 36 30kW UPS systems to store a my assumed 50% excess, which you have not specified. I would suggest that you contact someone and have them configure a customized installation.
TTFN
Is not it better to use lead acid batteries with high discharge depth?