I have a question regarding retaining wall design. I have a proposed multistory structure that has one wall that is a retaining wall. Normally I would design the wall for two conditions, freestanding and propped (by the building). In this particular instance, I do not believe I will be able to develop enough resistance in the structure to resist the forces contributed by the wall (it will be cost prohibitive).
In thinking about this, if my wall is cast in place.... And then back filled prior to construction of the building (allowing for any movement to take place at the top of the wall) then the building is placed, will I end up with any loads from the wall being transferred into my structure (not counting surcharges)? To me it seems like the wall will be stressed and deflect. Then once the building is constructed on this deflected wall then there will be no additional load transfer from the wall into the building structure.
I have a question regarding retaining wall design. I have a proposed multistory structure that has one wall that is a retaining wall. Normally I would design the wall for two conditions, freestanding and propped (by the building). In this particular instance, I do not believe I will be able to develop enough resistance in the structure to resist the forces contributed by the wall (it will be cost prohibitive).
In thinking about this, if my wall is cast in place.... And then back filled prior to construction of the building (allowing for any movement to take place at the top of the wall) then the building is placed, will I end up with any loads from the wall being transferred into my structure (not counting surcharges)? To me it seems like the wall will be stressed and deflect. Then once the building is constructed on this deflected wall then there will be no additional load transfer from the wall into the building structure.






RE: Retaining Wall Design?
I am not sure about rules of thumb, but there is a distance from the base of the wall, beyond which the building surcharge will have no effect on wall loads.
RE: Retaining Wall Design?
I am talking about the other way around. I want to use the retaining wall as a wall for one side of the building (have 3 sides steel framed with metal panel and the other being a concrete retaining wall).
RE: Retaining Wall Design?
RE: Retaining Wall Design?
You don't HAVE to dump that extra lateral load into your building, but you'll have to detail the bearing condition at the wall to allow it to move in the direction required and then design the wall and footing as a cantilevered retaining wall (with the applied axial stem load).
RE: Retaining Wall Design?
RE: Retaining Wall Design?
This is just for a proposed structure. I told the client that you should not attache the structure to the top of the wall if it is designed as a conventional cantilever retaining wall. This wall was proposed to be 24' tall and I would expect to have large lateral forces induced into the wall if our structure is attached at 12' and 24' to the wall. I would guess that you would end up with around 12,000#/ft of wall length as a force into the LFRS.
I was wondering if the wall was constructed and back filled allowing the deflection to take place... do you still have to include the forces (from the propped wall condition) in the design of the LFRS if the deflection has take place prior to construction of the building?
RE: Retaining Wall Design?
If the retaining wall is designed to resist the earth pressure without help from the building, then the building must be capable of accommodating the time dependent deflection of the retaining wall.
BA
RE: Retaining Wall Design?
The question about the retaining wall deflection stopping I guess is part of the question. Under normal conditions (what ever that means... not clay I guess) does a retaining wall continue to deflect over time or does a majority of the deflection take place withing the first few days after back filling?
RE: Retaining Wall Design?
If the wall is non-yielding (supported at the top by one of the building floor diaphragms), then the building sees all of the load from the wall.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
RE: Retaining Wall Design?
So, if I have a diaphragm at 12' and 24' that are constructed and poured 2 months after the wall is backfilled then the diaphragm will only see lateral loads from the surcharge loads placed on top of the grade?
RE: Retaining Wall Design?
There will be a small amount of long term additionaql load due to any creep of the wall, but that should be negligable.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
RE: Retaining Wall Design?
RE: Retaining Wall Design?
BA
RE: Retaining Wall Design?
I also think if possible I would design a horizontal expansion joint where your structure ties into the wall. I would think with almost any floor diaphragm and a decently stiff lateral force system, that if that wall begins to deflect that you will be putting unintended lateral loads into your diaphragm.
RE: Retaining Wall Design?
RE: Retaining Wall Design?
That being said, maybe there could be a compromise here. Perhaps the lower 12 feet could be a yielding wall, the area with the greatest lateral pressure, and the upper 12 foot story a non-yielding basement wall. Outside of the surcharge load, this mix could reduce the total lateral pressure of a full non-yielding wall by 2/3, depending on the soil pressure diagram.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
RE: Retaining Wall Design?
My client is looking to take the job over from a previous owner. He showed me some preliminary drawings clearly showing a tapered cantilever wall. In my mind it can't be done without taking the forces into the building and at 12000#/ft or somehow designing the wall for horizontal slip at the connection between the diaphragm and the wall.... very tricky. I just wanted to make sure I wasn't being overly conservative.
RE: Retaining Wall Design?
So we lost out on the project to another engineering company. My client must not have been happy with the way I presented my information to them. I had proposed using a buttressed retaining wall in lieu of a cantilever retaining wall. The engineering company who won the job proposed a counterfort retaining wall which the client seemed to like better (I thought they were the same thing). The other engineering company who is designing the building is not considering any loading from the retaining wall into the buildings LFRS. They are saying that the deflection of the wall will take place prior to the building being erected therefore; you do not have to consider soil loads in the design of the LFRS.
RE: Retaining Wall Design?
RE: Retaining Wall Design?
So maybe in 5-10 years you will have a forensic job!
RE: Retaining Wall Design?
Unfortunately I am still very involved even though we were not awarded the job. I was asked to help with some aspects of the job with my responsibilities growing day by day (don't know how my company came to that decision). This is how I know what is specifically happening with the design of the wall.
Ugh.......
RE: Retaining Wall Design?
It isn't a one time static thing.
BAretired is correct that it is really an indeterminate problem in that SOME of the active pressure will engage during construction (not the full design active pressure all at once).
After construction, due to thermal changes, moisture changes, near-sourced vibrations, etc. the soil will consoltidate over time and add to the pressure on the wall. And with the addition of the building frame, you then might be approaching a more "at-rest" condition than active.
This pressure will be shared by the wall stiffness and the building's frame stiffness in direct proportion to those stiffnesses.
The rate, and amount of the soil pressure is difficult to pin down - I'm not sure your average geotech could get a fully accurate number.
RE: Retaining Wall Design?
So what you are saying is that even though you have the GC compact the soil to 95% due to environmental conditions, you may end up with more compaction or soil movement that gives you more pressure against your wall?
I find it hard to believe that a retaining wall is going to be more "stiff" than a steel brace frame or masonry shear walls. So I would be inclined to believe that you would end up with some soil loads induced into the LFRS of the building.
RE: Retaining Wall Design?
My entire career has been in Florida where we mostly have cohesionless sand, and you can't much dig a two foot hole without it collapsing continuously. I have always had my doubts about this idea of soil pushing against a wall, the wall moving away, and that is the end of it...
RE: Retaining Wall Design?
RE: Retaining Wall Design?
About a week ago I received the geo. report for the project. According to the report, they recommend an angle of internal friction of 32 degrees. From the test pits that they dug, you can see that the soil on site appears to be a gravel/sand or sand/trace of silt mixture. There are also some concerns with bedrock in the area but they do not believe that they will have bedrock problems within the building footprint.