Parallel XMRs PU calc
Hi Ladies and Gents
happy Holidays
Can please somebody explain how per unit calculation  will be done  for two transformers in parallel ? one is off turn ratio .
RE: Parallel XMRs PU calc
Off turn ratio, = the open circuit voltage difference will cause a circulating current, limited by the impedance of both transformers = smoking hot
Bill
"Why not the best?"
Jimmy Carter
Treat the voltage difference caused by the turn ratio difference as a voltage source in one leg of the parallel network.
Why would you want to do that?  It will omly cause you problems.
Alan
Is this a correct example, jghrist:
Two transformers @2%Z with a voltage unbalance of 4% will have a circulating current of 100% rated current? Not good.
I have corrected circulating current issues a number of times but I have never measured the current or voltage. It was always a case of recognizing the issue and then making the issue go away as soon as possible.
Bill
"Why not the best?"
Jimmy Carter
Bill,
I believe that is a correct example.  I agree that the situation should be avoided.  Sometimes making the issue go away is not simple.
I have used this approach to calculate circulating currents when temporarily paralleling transformers that have different ratios and can get close but not exactly the same ratios with taps.