Hey guys,

Chapter 14.6 Minimum Wall Thickness

I'm designing a 110ft x 45ft x 10ft tall concrete cooling tower basin. Above ground. The owner wants it designed per ACI 350. Hypothetically, if my analysis tells me that an 18" thick wall is sufficient for flexure and shear, do I have to meet the "nor less than 1/30 the least distance between members that supply lateral support" requirement?

That would be 110ft x 0.0333 = 3'-8" thick!

If it was a 60ft long wall, it would require a 2'-0" thick wall! Can I get around this requirement?

I know the answer to this would be buttresses, wingwalls, or pilasters, but I'm trying to get away without them.

Who can help? Thanks.

-JMarch

RE: ACI 350-06 Minimum Wall Thickness Requirements

I do not have full copy of ACI 350 in my hands, but having looked at the 14.6.1 & .2 provisions, the short answer is "yes". The owner has already said that they want it designed to that criteria, and the minimum is the minimum, so don't try to save money which they feel they need to spend.

If you feel the need, economize elsewhere, by selecting less expensive details, for a quicker build, easier construction, and more durability.

RE: ACI 350-06 Minimum Wall Thickness Requirements

(OP)
The owner wants to maximize speed of construction and economy I'm exercising due diligence. Out of all of the references I have, this is the only thing that gives a minimum thickness based solely on length of unsupported wall.

-JMarch

RE: ACI 350-06 Minimum Wall Thickness Requirements

110' is a long way to span a wall.  Can't you build it as a cantilevered wall?

RE: ACI 350-06 Minimum Wall Thickness Requirements

(OP)
sorry I left that detail out. yes it is a cantilever wall

-JMarch

RE: ACI 350-06 Minimum Wall Thickness Requirements

For a cantilever wall, isn't the "member providing lateral restraint" the base slab?....which is continuous.

 

RE: ACI 350-06 Minimum Wall Thickness Requirements

JAE is correct, of course.  A cantilevered wall could be miles long, and the thickness required would be unrelated to the length.

RE: ACI 350-06 Minimum Wall Thickness Requirements

(OP)
It was unclear to me, that's why I consulted the experts here. I see now in section 14.1.2 where it says "Cantilever retaining walls are designed according to flexural design provisions of Chapter 10..."

Thanks all for your input.

-JMarch

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources