Heat Exchangers and Pumps

Heat Exchangers and Pumps

Heat Exchangers and Pumps

(OP)
Hello Folks, I am designing a chill water system where my cooling load capacity is over 500 tons. I am installing 4 heat exchangers (plate frame) my process loop will have a flow of over 300 gpm at a pressure of 75 psig (at the discharge of the heat exchangers). I have asked several experienced engineers in the fluid flow field and there are mix opinions on where to place the main circulation pumps. Should I place them on the supply side or the return side of the heat exchangers? Can you elaborate on your answers? Thanks in advance for your tips.  
 

RE: Heat Exchangers and Pumps

What's between the return side and the supply side?

RE: Heat Exchangers and Pumps

(OP)
My Process Equipment, the ones that need the chill water to operate i.e. Compressors, Vacuum Pumps, Water Stills, etc. Thanks for your prompt response.

RE: Heat Exchangers and Pumps

You show no storage tanks for either chilled water loop.  Is this correct?  I assume you have two water loops out of concern of contaminating the process stream and not wanting to put that water through the chiller?
 

RE: Heat Exchangers and Pumps

(OP)
Yeap,no storage tanks and there are two separate loops, see my attached drawng.

RE: Heat Exchangers and Pumps

I rather prefer option one since the power consumption will be lower since the density of the water pumped will be higher (due to the lower temp). Although this difference will not be very high since the density of the water does not experience great changes.



 

RE: Heat Exchangers and Pumps

Well, you've got to put it at least where you run out of pressure due to the head loss of all that stuff.  But I'd also put it where you still have a low enough temperature to be sure that your NPSHa is still good, not for saving power based on the water density.  Rembering all the while that the lower the pressure you can get the most expensive piece(s) of equipment to operate at, the lower the pressure rating will be and the lower the cost of that equipment will tend to be too.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources