Plant Blowdown Starting Pressure

Plant Blowdown Starting Pressure

Plant Blowdown Starting Pressure

(OP)
We've been instructed to blow down the facility to the lesser of either 700 kPag or 1/2 the design stress of the equipment in 15 minutes or less.  

Does anyone know if the starting point is system design pressure (i.e., MAWP) or normal operating pressure?  API RP521 is somewhat vague in this manner and it's not real clear.  It does make a significant difference because of the large margin between normal and MAWP in some of the vessels.

RE: Plant Blowdown Starting Pressure

I'd design for the normal pressure.  If it takes 16 minutes to get to the desired point from MAWP, so what.  15 minutes is just an arbritary number to begin with anyway.

There is more concern for rate to me.  If you have to blowdown a million Kg in 15 minutes that is one thing versus 1000 Kg.  Most chemical plant limit the rate to a point of either a flare limit or if to atmos, 10,000 kg/hr.

RE: Plant Blowdown Starting Pressure

(OP)
Thanks dcasto - I'm with you on this one and was hoping you'd jump in on this discussion but I have no way of reaching you directly.  I'm thinking the same thing - but the client is being somewhat conservative with design pressure as a starting point.  

We're still limiting flare tip mach to 0.5 so no concerns there and we still do detailed piping pressure drop calc's to check backpressure on the system.

RE: Plant Blowdown Starting Pressure

Hi Maddocks,

I think the clients Design practice should take precedence on this.  Exxonmobil, for instance, requires that you start blowing down from the maximum operating pressure.  I have encounted clients to prefers PSHH set point, which can be like 90% of the MAWP.

But for compressors, you have to start from the settle out pressure.

Buchi

RE: Plant Blowdown Starting Pressure

I think it depends on if the blow down case is a fire case - if so normally pahh could be the starting point - and remember to allow for additional boil off. I think HYSYS can do this for you.

Best regards

Morten

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources