Question on a certain calculation
I have a question on a certain calculation in the
Design of Anchor Reinforcement in Concrete Pedestals by Widianto, Patel and Owen.... I found it in google and I also uploaded this on the link below,
my question is that on page 14 of the article, there's a formula involving the bearing area:
Abrg = 0.866*2^2-5/4 * 1.25^2
i know that "2" came from the anchor head, and "1.25" is the diameter of anchor, but where did they get the "0.866" and "5/4" respectively?
thank you in advance!
Poems are made by fools like me, but only God can make a tree. engineers creates wonderful buildings, but only God can creates wonderful minds
RE: Question on a certain calculation
There's a typo in the formula and it affects the answer.  It should be pi/4, not 5/4. The bearing area of a 1.25 diameter bolt with a heavy hex head is 2.237 in^2.
As far as the .866, I don't have the formula in front of me, but that must be the factor to calculate the area of a hexagon.
I can confirm JedClampett's statement:
for a Hexagon, A = 0.866*d^2
d = distance across the flats.
chichuck
thank you very much