Can Any body tell in simple way - How to cross check the actual tonnage of a cooling tower installed already ?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Cooling Tower Capacity cross checking
|
RE: Cooling Tower Capacity cross checking
Using the model number, you can estimate the performance from the manufacturers performance specs, assuming you know or can assume CWS&R temps (often typical), local design wetbulb (refer ASHRAE tabulated by location), and flowrate (from pump).
There are lots of other factors which can throw a tower off-standard spec but this should get you ballpark.
You are far better off looking at drawings for schedules, or calling the local rep with the serial number.
RE: Cooling Tower Capacity cross checking
Cooling tower capacity=the tower mass flow ratexTemperature difference across the towerxspecific heat of water(based on actual measurements)
Measure the local wet bulb temperature and refer to the Tower performance charts to obtain rated capacity.
The variation between the two values should not be more than 5%(Not sure about this better check CTI stds)
Cooling tower capacity is a function of local wet bulb temperaure and therefore capacity is not mentioned on the name plate.
RE: Cooling Tower Capacity cross checking
Cooling towers so rarely operate at the rated conditions, taking measurements is nothing more than spot check. A year or two of trending is a different story.
RE: Cooling Tower Capacity cross checking
Remember though what KiwiMace is saying about rated conditions.