Folks,
I wanted some clarification on the longitudinal reinforcing requirements for piles. The IBC seems to be pretty clear on what the reinforcing requirements are for SDC C and lower and SDC D and higher.
However, my question stems from a design standpoint.
The geotechnical engineer usually gives the flexural length of the pile (or by request), the allowable compression/tension values and shear capacities. We as structural engineers are required to design the reinforcing for the piles.
1. Assume I have a cluster of 40 piles for a shear wall pile cap subject to shear, axial and bending. The T/C loads in a pile can be easily calculated. The shear loads can be assumed to distributed equally to all piles.
LONGITUDINAL STEEL FOR MOMENT:
How is the longitudinal reinforcing in the pile calculated? Is it calculated based on (shear load on pile * flexural length)? If so, then should the pile be treated as a cantilevered beam/column with axial load and moment with an unbraced length = flexural length? We can either use a pile with a fixed head or pinned head which will change the moment values.
I have commonly seen piles with cage of 6#6 bars with #3 hoops extending 1/3 the length of pile + a full length bar. I don't know if that's just common practice that works for almost all conditions.
LONGITUDINAL STEEL FOR TENSION:
The tension capacity of a pile comes from skin friction. The shaft sheds tension into the surrounding soil based on depth of penetration. The tension in the pile is zero at its tip. Can the quantity of reinforcing be dropped based on how much tension exists in the pile?
SHEAR CAPACITY OF PILE CAP:
I assume the shear capacity of a pile group and pile cap is a function of the shear capacity of pile + passive resistance of pile cap + sliding resistance of cap.
Is it common to use the summation of all three to calculate the shear capacity? Or do you only use shear capacity of pile + passive of pile cap?
Sorry for the long winded post. I really wanted to summarize all my questions in one post.
I wanted some clarification on the longitudinal reinforcing requirements for piles. The IBC seems to be pretty clear on what the reinforcing requirements are for SDC C and lower and SDC D and higher.
However, my question stems from a design standpoint.
The geotechnical engineer usually gives the flexural length of the pile (or by request), the allowable compression/tension values and shear capacities. We as structural engineers are required to design the reinforcing for the piles.
1. Assume I have a cluster of 40 piles for a shear wall pile cap subject to shear, axial and bending. The T/C loads in a pile can be easily calculated. The shear loads can be assumed to distributed equally to all piles.
LONGITUDINAL STEEL FOR MOMENT:
How is the longitudinal reinforcing in the pile calculated? Is it calculated based on (shear load on pile * flexural length)? If so, then should the pile be treated as a cantilevered beam/column with axial load and moment with an unbraced length = flexural length? We can either use a pile with a fixed head or pinned head which will change the moment values.
I have commonly seen piles with cage of 6#6 bars with #3 hoops extending 1/3 the length of pile + a full length bar. I don't know if that's just common practice that works for almost all conditions.
LONGITUDINAL STEEL FOR TENSION:
The tension capacity of a pile comes from skin friction. The shaft sheds tension into the surrounding soil based on depth of penetration. The tension in the pile is zero at its tip. Can the quantity of reinforcing be dropped based on how much tension exists in the pile?
SHEAR CAPACITY OF PILE CAP:
I assume the shear capacity of a pile group and pile cap is a function of the shear capacity of pile + passive resistance of pile cap + sliding resistance of cap.
Is it common to use the summation of all three to calculate the shear capacity? Or do you only use shear capacity of pile + passive of pile cap?
Sorry for the long winded post. I really wanted to summarize all my questions in one post.






RE: Pile Reinforcement
Rewording what above, and aiming reinforcement, your quoted list above is more than anything the list of results of your analysis, that must be as complete as to reasonable portrait the particularities of required design for your structure.
RE: Pile Reinforcement
RE: Pile Reinforcement
Bascially like any other member. If good soil it is a short column fixed on both ends with a moment based on shear per pile and the point of fixity provided by the geotech. Then PCA Column with cover per the code.
Shear resistance is combo of the items that you indicated with the limit for the pile based on the recommendations of the geotech. Then check shear stress in pile without reinforcement. Don't think I ever had a condition when the shear stress was very high since the limitations of the soil are relatively low.
How far the cage extends depends on the required tension capacity and moment capacity. I extend the cage at least a few feet past the point of fixity. On a high capacity tension pile the amount of reinforcement required will likely require that the cage extends full length to a rock socket. I guess that you could drop a few bars as you go down if it is a friction pile but I haven't ever done that. The geotechs are estimating the relative friction/bearing resisteance and they won't know for sure until they do the load tests.
In a compression pile something like you indicated seems about right unless you are counting on the compression steel to contribute to the capacity of the section. If it is a high capacity pile I would use more steel. In a condition where the cage stops I always add one bar full length to be sure the hole didn't collapse.
RE: Pile Reinforcement
RE Flexural design:
Interesting that you say the geotech performs the analysis. I always ask the geotech for soil properties and then run through my own analysis and design. If the pile is behaving like a column then it must be designed as a column.
RE Termination
If reinforcement is no longer required then it is acceptable to terminate the reinforcement.
RE: Pile Reinforcement
The allowable shear loads and axial loads are given by the Geotech. How do you folks address the following issues?
1. Do you design the piles for the ultimate shear (Allowable * 2)? Or do you design it for the shear per pile based on ASCE/IBC load combinations (~1.6 factor)?
2. Similarly, for P-M interaction, do you design it for ultimate axial load and moment due to ultimate shear * flexural length? Or do you use values based on actual load combinations?
3. For tensile loads, do you use:
As,reqd = (ultimate tension in pile) / (0.9*60 ksi)
[or]
As,reqd = (geotech allowable tension capacity) / (24 ksi)
RE: Pile Reinforcement
RE: Pile Reinforcement
I ask the geotech for the l-pile (or similar program) output. They can give you the shear and moment diagram for the pile with whatever lateral load you want on it. Then you can just design for those moments and shears. As for axial I am pretty sure (not positive) that the ACI 543 gives you allowables for the axial load.
RE: Pile Reinforcement
we provide maximum bases forces (shear, axial compression, axial tension, and moment if applicable) to the geotech. He does a run in L-pile to and gives us shear and moment diagrams for the caissons. You have to be careful here, though. If you have grade beams the geotech will try to say the top of the caisson os restrained to keep deflections under control. This puts a very large moment at the caisson/grade beam joinT and can cause a lot of congestion. It's best to leave the caissons unrestrained, if you can.
We take the shear and moment diagrams and design them just like a column - always as a short column.
RE: Pile Reinforcement
Unless you have large lateral forces that benefit from passive soil pressures, I typically find that the pile stresses are relatively small since the design is governed by the soil characteristics.
Brad
RE: Pile Reinforcement
1. Do you use a overload multiplier such as 1.6 and the calculate using Pu / 0.9Fy?
2. Do you use the provided tension capacity of the pile and use a stress of 24 ksi or some other number i.e. P / 0.6Fy