11kV Test transformer
We have a client that requires a 415V/11kV transformer for testing 11kV substations under no load conditions in his factory before shipping the product to customers.
So we need a 415V to 11kV transformer for powering a 1.5MVA 11kV to 1kV substations.
I suspect because this is being done under no load conditions our main concern would be to have a transformer big enough to deal with the inrush current requirements for the 11kV/1kV transformer.
So for example : the 1.5MVA 11kV/1kV transformer and assuming 12 x the rated current as the inrush current for 100msec -> 1.5MVA rated current is 78A on primary side -> 12 x 78A = 936A.
I then assume the 415V/11kV transformer can deal with 40 times the rated current for a short period of time without damage (the average short circuit withstand rating). So 936A/40 = 23.4A. So by this logic and calculation the 415V/11KV transformer needs to be at least a 11kV*23.4A = 257,400kVA or 260kVA.
So here is my question: Am I calculating this correctly ? (The calculated size this seems a little BIG to me.)
RE: 11kV Test transformer
I would hazard a guess that it is a bit big.
Ausphil