(OP)
Our design presently shows that the building steel columns are used as ground conductors (criteria for down conductor requrement are met). Therefore, the aerial rods are bonded to the vertical steel columns. However, on grade, the steel columns are directly bonded to the unmderground grounding grid (plant electrical ground grid).

As far as I remember, we used to drive dedicated ground rods to each down conductors. In our case, I could have expected the steel column frame at grade connected to its dedicated ground rod and from this ground rod it will be bonded to the plant electrical grid. Is my concept correct? We used BS 6651 long time ago with that installation.  

RE: Down Conductors To Ground Rod Question

(OP)
Further to my question, can the underground ground rods which are directly connected to the lightning down conductors be interconnected to from a ring grid and be used as the Electrical Ground Grid for the building itself?

Appreciate your comments

RE: Down Conductors To Ground Rod Question

I'm not sure I understand your first question. The answer to the 2nd question in the U.S. would be yes. Not sure about Canada, or wherever you are.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: Down Conductors To Ground Rod Question

(OP)
On the first question:

The down conductors are bonded directly to the electrical grounding grid that encircles the building. Is this allowed?

Is it going to be an acceptable installation if the down conductors are connected first to their associated ground rods and then these rods will each be bonded to the overall electrical ground grid?

----------------------------------------------------------

The answer to the 2nd question you mentioned, did you meant my 2nd separately posted question: "Further to my question, can the underground ground rods which are directly connected to the lightning down conductors be interconnected to from a ring grid and be used as the Electrical Ground Grid for the building itself?"

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources