Smart questions
Smart answers
Smart people
Join Eng-Tips Forums
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

elfman (Mechanical) (OP)
16 Nov 10 13:12
Strange request.  I am trying to get a Micrologix 1400 to communicate with a Lenze SMVector VFD via Ethernet/IP.  I am writing everything in RSLogix 500.  I have never done this before and am looking for suggestions, recommendations, and or examples.

I am trying to get started with the code and need some examples of communicating via Ethernet/IP.  I realize I have indicated a very specific hardware setup that few have probably delt with but examples that show principles will be much appreicated.

Thanks in advance.
djs (Electrical)
18 Nov 10 12:56
You need to find out what the interface is. Then program MSG instructions using CIP type.  
jde777 (Electrical)
19 Nov 10 1:57
eeprom (Electrical)
7 Dec 10 15:08
Elfman,
I've done this many times using rockwell VFDs, so I may be able to help.  A very basic rundown of how this all works is as follows:

The VFD has an ethernet card on it.  The ethernet card will be programmed with a static IP address so that it can be seen by the PLC which is also programmed with a static IP address.  The ethernet card allows some of the VFD parameters to be read or written to.  The VFD will have some parameters which are data links.  These links are memory spaces which are in constant communication with the ethernet card.  The links are empty until you assign a parameter value to them.  The links act as pointers to VFD parameter values.

The 1400 can talk to the ethernet card through a messaging file.  You need one file to send information, and another file to receive information.  The PLC has to have a static IP address which is accessible to the VFD.

The 20-comm-e manual (publication 20COMM-UM101D-EN-P) is a manual for rockwell's VFD communication cards.  On pages 4-38 to 4-44 there is an excellent example of how to use messaging files to talk to a powerflex 70.  I recommend that you read this example.  Also, on page 5-3 is a diagram showing how the 20-comm-e points to the data links in the VFD.  This will show you conceptually how this whole thing comes together.  You will have to find the manual for your specific VFD in order to find the actual mapping.

Good luck.
 

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close