Companion CLF with Cutouts Practices
2

Companion CLF with Cutouts Practices

Companion CLF with Cutouts Practices

(OP)
Our utility is looking at its practice of installing a CLF with a NEMA rated link (K) Cutout at 12.47KV O/H. We install them wherever the fault current exceeds 5KA sym. Our standards say our lowest rated cutouts are rated 6.2KA sym. Hearsay notes we install them due to dist. tranformer withstand but we have no documentation to support this. An IEEE T&D survey states utilites use them for both cases without any information on levels of transformer withstand ratings.
What is your utility practice?
  

RE: Companion CLF with Cutouts Practices

Not sure of the utility companies, but it is a common practice to protect commercial/industrial transformers. It is not because of lack of transformer withstand ratings, but the low SCCR (interrupting) rating of the K links, which can be as low as 2.5 kA. CLF are generally sized larger as a backup to the links.

Rafiq Bulsara
http://www.srengineersct.com

RE: Companion CLF with Cutouts Practices

It's been a long time since I worked on transformer protection, but they have an (I**2)t  withstand rating.  The use of the CL fuse is to limit the energy pass through.   
I've seen pole mount transformers that exploded, showering oil everywhere, due to too much energy.  
CL fuse use is very common in padmounts where an event could be catastrophic.

Jim T

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources