Floor box 'support' prior to slab placement?

Floor box 'support' prior to slab placement?

Floor box 'support' prior to slab placement?

(OP)
The Elec. contractor wants to place his (2 per classroom) die cast alloy floor boxes upon home made galvanized metal strap 'chairs' attached to the subsoil w/spikes.

This blows the concept of avoiding a path for electrolysis or corrosion.

AOR says its 'means and methods'.

I think it wrong.

Your opinions please.

(I am also posting this in the Structural Forum)

Thanks, Steve (IOR)

RE: Floor box 'support' prior to slab placement?

The preferred method is a small rat slab at the box location and then use the leveling screws to place the top of the box correctly in relation to the finish floor level.  

RE: Floor box 'support' prior to slab placement?

If there is a vapor barrier such as a plastic sheet under the slab, this method will not be allowed as it would puncture the vapor barrier. The concrete in contact with the box and the rebar will probably provide a better ground path than a couple of spikes in the subsoil. (Google "Ufer" grounds").
In addition the box may be fed by a galvanized, grounded conduit.
I agree with David in regards to the best method, however this method may depend on cooperation from the concrete contractor and such cooperation is not always forthcoming.
As for corrosion, I don't see the straps causing a problem.
I have seen corrosion problems but almost always as a result of poor quality porous concrete. With good quality concrete the straps may corrode below the concrete but the corrosion will not travel into the concrete more than a small part of an inch, at least in our lifetimes.
However if you desire rat slabs as David suggests, I would suggest negotiation and compromise on this job and for future work, be sure to specify the method of mounting floor boxes.
A contractor I was with years ago would drive short pieces of 1/2" EMT into the sub soil and wire them to the sides of the floor boxes. We never had a problem or a complaint.
I see a wide range of quality in jobsite methods. When the customer is willing to pay for quality, David's suggestion would prevail. With a building built "On the cheap" by the lowest bidder, as long as there is a box in the floor that is almost at the correct level and close to the correct location, the installation may be acceptable.
 

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Floor box 'support' prior to slab placement?

(OP)
Thank you for your interest in this.

with anothers help I found this....

"CEC Title 24 300.6 (A) and 358.10 (B). Ferrous raceways may be used in direct contact with soil or in concrete but must provided with corrosion protection where subject to severe corrosive influences. You must review your soils report to determine if there are any severe corrosive conditions noted. You must also check your approved plans and specification for limited uses for ferrous or non-ferrous EMT. I would raise concerns where there are acidic soils or a high water table or saturated clay soils but the code seems clear."

Inspector Steve
DSA, OSHPD, Inspector
So. California.

RE: Floor box 'support' prior to slab placement?

Thank you for the update, Steve.
Yours
Bill

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources