so-lo run Compressor 2600 kW
so-lo run Compressor 2600 kW
(OP)
If we need to start for so-lo run Compressor 2600 kW ,11 kV.
How big diesel generator, we need to prepare for testing.
Thanks
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
so-lo run Compressor 2600 kW
|
RE: so-lo run Compressor 2600 kW
See FAQ237-766: Generator Sizing for a Motor Load
Rafiq Bulsara
http://www.srengineersct.com
RE: so-lo run Compressor 2600 kW
Starting the compressor only with no other loads: Possibly 6500 kW
A smaller generator may be possible in the case of special circumstances or combined generator/compressor starting.
For VFD starting use 5200 kW. Minimum 200%, to allow for distortion wave form and its effect on the Automatic Voltage Regulator. (AVR)
Bill
--------------------
"Why not the best?"
Jimmy Carter