so-lo run Compressor 2600 kW

so-lo run Compressor 2600 kW

so-lo run Compressor 2600 kW

(OP)

If we need to start for so-lo run Compressor 2600 kW ,11 kV.
How big diesel generator, we need to prepare for testing.

Thanks
 

RE: so-lo run Compressor 2600 kW

Safe choice: 7800 kW
Starting the compressor only with no other loads: Possibly 6500 kW
A smaller generator may be possible in the case of special circumstances or combined generator/compressor starting.
For VFD starting use 5200 kW. Minimum 200%, to allow for distortion wave form and its effect on the Automatic Voltage Regulator. (AVR)

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources