Transferring of wind loads by bracing roof trusses
Is there any method of transferring bracing forces through the roof trusses if the gypsum board ceiling is ineffective. My building code only allows gypsum board to be used for spans up to 9.0m (30'). I have a light gauge metal sheet roof which cannot be assumed to act as a diaphragm. Is there any other method out there to transfer the wind loads?
RE: Transferring of wind loads by bracing roof trusses
Outside of that, you'll have to get a bit more unconventional with blocking and x-bracing, but chasing the stress paths could be a nightmare.
Plywood diaphragm to the underside of the roof trusses (this will be the method that I go with).
Provide blocking and strap bracing to the top chord to create bracing in the roof plane.
Horizontal Trusses which I assume will be fixed to the underside of the roof trusses.
Because in this instance the roof pitch is very flat (3 deg), the majority of the racking force comes from wind force on external walls.
I am having a major dispute with the builder over this one.
You have been brought up correctly. Don't depend on the roofing. It is to shed water, not to brace the building. If you had a steeper roof, you could provide knee bracing to bring gable forces down to the ceiling. I know that in the States, they use continuous sheathing on the roof which serves as a diaphragm, but the ceiling is the most logical place for bracing. If you can't follow my earlier suggestion to engage more shear walls, try Ron's plywood ceiling level diaphragm or cross bracing.
I would trust metal roofing far more than gypsum board but definately not more than the 9m you mention..
htt
That aside, if you do not want to trust it then why not use metal strap bracing. Pryda do some heavy duty load rated strap.
Your reference is for metal roof deck, not for roofing. I've been practicing in Australia for 27 years, and have never used roofing for diaphragm action, and have never seen it used in that way except for very small garden sheds and the like.
thread507-270224: Providing lateral stability for wood frame building