Pre Eng building canopy

Pre Eng building canopy

(OP)
On top of the Exterior door, contractor install canopy. Size of canopy is 1.2mt wide and 1.8mt long. Because of snow drift, snow load on that canopy called for 10 Kpa.  Which engineer wants to confirm.
Is it make sense to consider 10kap load to design this small canopy?
Please share any thoughts
 

RE: Pre Eng building canopy

PEMBs are reputed to have essentially zero safety margin.  
Be careful what you hang it on.
 

Mike Halloran
Pembroke Pines, FL, USA

RE: Pre Eng building canopy

I note that you are from Alberta, Canada.  The Alberta Building Code provides snow loads and some guidance for this situation.  Why don't you use it to determine design criteria?  Most members of this forum don't know the conditions in your area, so you must make reasonable judgments on your own.  

It does not seem likely that a 10 kPa snow load on such a small canopy would have significant cost ramifications, so why not just stick with the code?

BA

RE: Pre Eng building canopy

Both of the above responses are right on target.  A PEMB has little margin to add anything.

As for 10kpa...yes, that's a bit high, but considering where you are located and the drift because of the geometry of the canopy, it is probably not unreasonable, since you wouldn't want the entry blocked by a collapse.

Do as BAretired noted...follow the code.  When you compute the drift, you'll find that because your canopy is short, your trapezoidal load distribution won't vary much from front to back of the canopy.

RE: Pre Eng building canopy

Can you use a separate support structure, as the  PEMB likely has little reserve to accomodate?

RE: Pre Eng building canopy

You might also consider sliding snow with impact if the upper roof slopes downard toward the canopy and the upper roof does not include a mechanism to alleviate this condition

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources