ASCE 7-10 Wind Load Cases
In Figure 27.4-8 of ASCE 7-10, it shows 4 wind cases you must check. Actually case 2 and 4 can be eliminated in some instances. Anyway, I can't find where they say "boo" about what you're supposed to do with the roof load. I'm thinking of a gable roof. Case 1 is pretty obvious since the wind is blowing either parallel or perpendicular to the roof ridge. But what about case 3 where you have a quartering wind? What I decided to do was use the full design roof pressure for the case when wind is blowing perpendicular to the ridge with the wall pressures shown in case 3. Any thoughts? Is this really not addressed or am I missing it?
RE: ASCE 7-10 Wind Load Cases
I think what Ron says is that Oblique directions will not be the controling factor for roof design, but longitudinal and transverse conditions will control the roof design. that does not means you don't need to put load on roof when you run oblique wind cases.
I believe you when you say it doesn't control the roof design but you still have to put something on the roof. I'm just surprised that ASCE 7 doesn't say anything about it.
As an example, it is sometimes easier to do a few hand calcs and develop the roof structure reactions, then apply those to an "open box" FEA model. That saves the time and effort to build each truss/joist/dummy beam for the roof into the model. It makes the interpretation of the results easier and also makes it easier to troubleshoot your model if you are working with a notoriously "buggy" FEA program. Depending on the complexity of your model, they can "blow up" on you pretty easily sometimes.
So, IMHO, ASCE 7 sets general parameters from which we are to use engineering judgment in the application of those parameters. They cannot set parameters with such site specific parameters as building geometry, building design parameters and other items that would be specific to your building, but they give you the tools to set those yourself.
In your case, you can do it either way you'd like. You might even want to try it a couple of ways so that you'll know the differences and can look for special cases. If you have built a full FEA model, it's pretty easy to change the load conditions. If you have a partial model, same thing. If you're doing it by hand...simplify!
http://www.iitk.ac.in/nicee/IITK-GSDMA/W05.pdf
I only have ASCE 7-05 but it sounds similar to the newer 7-10. It is my understanding that you take the loadings shown in Fig 6-10 (7-05) which include both wall and roof loads and apply them as shown in Case 1 - 4. So in case #3 you would apply 75% of the loadings from a transverse direction and 75% of the longitudinal direction.