Voltage Transformer Isolation
Voltage Transformer Isolation
(OP)
We have 132kV GIS switchgear with outgoing cables connnected. The cable needs to be tested at HV AC at 75kV. The voltage transformer is a fixed type above the cable box. Disconnecting mean are provided inside the cable box, but degassing would be required to remove that link.
Should the GIS be disconnected from the cable?
Should the GIS be disconnected from the cable?






RE: Voltage Transformer Isolation
Get the OEM procedures for that particular switchgear design and follow them. Is this an older existing installation or is new being just now commissioned?
rasevskii
RE: Voltage Transformer Isolation
What is the point of testing at 75KV AC as that is the normal operating voltage anyway? Usually a higher test voltage would be used:
Cable experts offered to comment here....