Synchronized generator with different nominal voltage

Synchronized generator with different nominal voltage

Synchronized generator with different nominal voltage

(OP)
Hi All,

Our existing generators are 11,000 V +/-5% output voltage. We set AVR 3% above nominal volt (11,350). Gens are running with voltage control set.

What do you think If a new gen 10,500 V +/-5% will be synchronized with existing system. It should run 8% over its nom volt.

Regards,
Sumadi

RE: Synchronized generator with different nominal voltage

If it doesn't trip, it will consume massive reactive power. Is the +5 % of the 10.5 kV machine an absolute limit?  

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Synchronized generator with different nominal voltage

I expect that you will be running on or above the V/Hz limit for continuous operation. If you aren't then the reactive capability of the machine will be severely limited if you push the terminal voltage up to 11kV. You will probably find that discharge activity is higher at 11kV than at 10.5kV.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Synchronized generator with different nominal voltage

Can't you adjust AVR of 10,5kV generator to 11kV? The machines we use have same stator winding for either 10, 10,5 or 11kV.
I don't know if your generator can do that, but check with generator manufactor.

RE: Synchronized generator with different nominal voltage

I'm thinking massive circulating (reactive) current, potential AVR instability and maybe a little partial discharge.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources