serie rating of MCCB
We have a place with a lot of MCCB Westinghouse type F and FB and some Cutler-Hammer type FD and FDB.
The capacity of these breaker are 14 or 18 kA, but the short-cicuit current is way over.
The breakers are in serie with a current limiting fuse, type RK-5.
I have found serie rating chart for the Cutler-Hammer breaker with the fuse, but not for the Westinghouse.
Does anybody have this information available?
RE: serie rating of MCCB
looking at the fuse curves, it appeared that the fuses would limit the fault current, but the dynamic impedance imposed when the breakers started to open ruined that thought process.
Do you think that we cannot rely on this kind of chart?
David Castor
www.cvoes.com
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
I was thinking maybe someone have old litterature about this.
I think that it wasn't a bad conception at the time and people really take short circuit current into consideration. That's why they put current limiting fuse in serie, but without any written information I can't really make assumption. But maybe in the old days testing wasn't done for this setup like today as jraf said. Maybe they only made some calculation?
If it was a couple of breaker i wouldn't mind, just change it. But here are several hundred.
Rafiq Bulsara
http://www.srengineersct.com