NFPA 13 heat zones

NFPA 13 heat zones

NFPA 13 heat zones

(OP)
How far away should I keep the fire sprinklers from an outdoor, surface-mounted heater? These heaters will be installed in the outdoor patio areas on a house but there is nothing in 13D that describes this particular appliance.

RE: NFPA 13 heat zones

Did you look in 13???

RE: NFPA 13 heat zones

Being an outdoor space and using 13D are sprinklers even required?

RE: NFPA 13 heat zones

8.3.2.5. Nfpa 13 2002 edition also same section table

And also bump to higher temp head

RE: NFPA 13 heat zones

(OP)
Thanks, cdafd, I looked in NFPA 13 8.3.2.5 and that section was very helpful. My sprinklers will have to be within 7 feet of the heat source so I'll bump the sprinks up to 286 deg.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources