Testing of motor following presumed switchgear fault

Testing of motor following presumed switchgear fault

Testing of motor following presumed switchgear fault

(OP)
We started a 13.2kv 7000hp horizontal sleeve bearing motor driving a centrifugal pump.  As shown in flow traces, the pump ran for about 4 seconds and developed discharge pressure.  At that point there was some event which resulted in something resembling an explosion in the switchgear cubicle feeding the motor (caused the switchgear to bulge), and obviouisly a motor trip.

Let's assume the cause of the fault is in the switchgear and is troubleshot and found. (not yet there, but looking ahead)

Let's further assume the motor meggers and bridges ok.  (same caveat).

Would you say that any further testing is required to conclude that the event did not damage the motor?

(It occurs to me that there may have been abnormal surge voltages and also currents associated with motor feeding the fault)

=====================================
(2B)+(2B)'  ?

RE: Testing of motor following presumed switchgear fault

Nice accidents you have, Pete!

Would like to see the recordings.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Testing of motor following presumed switchgear fault

I think before concluding (and of course after the assumed successful testing) that the motor was undamaged, that I would verify that the motor turns freely.  Although unlikely, it is always possible that the failure of the switchgear was triggered by a mechanical obstruction sucked into the pump.

RE: Testing of motor following presumed switchgear fault

I have the same feeling as potteryshard, the accident is somehow related to the motor-pump and the process, combined with some bad device in the switchgear.

I would run the motor de-coupled from the pump first, even if it is cumbersome and time consuming to do, to see and show that the motor itself is good. (after successful pre-tests  mentioned earlier).

Rafiq Bulsara
http://www.srengineersct.com

RE: Testing of motor following presumed switchgear fault

And of course check the pump and alignment...

 

Rafiq Bulsara
http://www.srengineersct.com

RE: Testing of motor following presumed switchgear fault

Pete,

Properly functioning switchgear can safely carry high overloads and can safely interrupt very high currents with no damage. If your gear is properly rated and the overcurrent devices function then there is little to no chance that a fault in the motor or process caused the fault in the switchgear.

However, I agree that when something like this happens and the equipment in question is very costly then testing is called for.

Electrically you will want to test the motor for grounds or shorts. A high potential tester and a surge tester would be the appropriate devices to use. You need to apply voltages  that are high enough to test the insulation and to find a fault if it exists. In most cases, the value chosen is 2E + 1kV = 26.4 + 1 = 27.4kV.   

Although there is no relation to the fault, since  the motor is going to be down for a while due to the switchgear repairs then it wouldn't be a bad idea to roll out the bearings for inspection if that hasn't been done in a while. If you perform the electrical tests and the bearing inspections then you can confidently say that the motor is good to go.

I am curious. Was this an across the line start using a circuit breaker or is it some form of reduced voltage starter, soft starter, or VFD?

 

RE: Testing of motor following presumed switchgear fault

(OP)
Thanks everyone.

We have no recordings of current. We use state of the art 1980's electromechanical relays.  We do have some 1-second samples of voltage magnitude which tell an interesting story.  The whole story is interesting and still unfolding, but there may be some commercially sensitive information (I am being intentionally vague). Maybe later more details will follow.  

=====================================
(2B)+(2B)'  ?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources