Contact vs. Non COntact Splices

Contact vs. Non COntact Splices

Contact vs. Non COntact Splices

(OP)
I have a question about contact splices. I understand that non-contact splices are allowed, if they are designed as non-contact splices. My question is if you have a designed contact splice, is there any tolerance for the bars to be not in full contact. I have been back and forth with a few people and I have done a bunch of searches, but I cant seem to find an answer.

Thanks,

RE: Contact vs. Non COntact Splices

Try ACI 318-05 12.14.2.3.

RE: Contact vs. Non COntact Splices

12.14.2.3 isn't very clear.  The contact/noncontact distinction makes it sound like there should be different procedures for the design of each.  Is a noncontact lap splice designed with the same procedure as a contact lap splice as long as the gap between the lapped bars is within the limits in 12.14.2.3?

RE: Contact vs. Non COntact Splices

There is no difference in contact or non-contact lap splices.  Wiring the bars together is the best way to assure that the bars are not displaced during placement of concrete, but other methods which secure the bars is permitted under the code.  Bars must be secured into position before and during concrete placement.

CRSI publication Reinforcing Bars: Anchorage and Splices paragraph 3.1.1 describes the contact/non-contact issue.

ACI 318 7.5.1 requires securing reinforcement prior to concrete placement.

John Turner CSP PE
CRSI Greater Southwestern Regional Manager

RE: Contact vs. Non COntact Splices

"ACI 318 7.5.1 requires securing reinforcement prior to concrete placement."--John Turner

This is what the code states, but in reality this rule is regularly flouted. A lot of dowels intended to anchor walls to footings are simply "wet-set"; unless of course, the RDP is present during installation and concrete placement and puts his/her foot down.

RE: Contact vs. Non COntact Splices

Wet setting dowels is a good way to get bad connections.  It is prohibited because, unless they are vibrated in before initial concrete set, there will likely be little or no structural bond development.  Vibrating them (which requires liquifaction of the concrete) prevents them from staying in place.  Once the concrete is stiff enough to hold, it is too stiff to consolidate properly around the bar.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources