Dear All,
I have very basic question, but make me inconfidence regard to speeding up induction motor. The existing nameplate is 600kW, 3.3kV and 2965rpm. We have to upgrade the feed pump system by installing VSD to control this motor up to max 3400 rpm. (operating will be 3100rpm)
The question is what is the effect of over-speed ?
Can I use the existing or have to replace with other motor?
For detail please see attachment.
Thank for your recommendation.
Regards,
Eskim
I have very basic question, but make me inconfidence regard to speeding up induction motor. The existing nameplate is 600kW, 3.3kV and 2965rpm. We have to upgrade the feed pump system by installing VSD to control this motor up to max 3400 rpm. (operating will be 3100rpm)
The question is what is the effect of over-speed ?
Can I use the existing or have to replace with other motor?
For detail please see attachment.
Thank for your recommendation.
Regards,
Eskim





RE: Speed up motor
I'm not sure the last part of that is valid. Some motor cooling fan designs are somewhat flat, so at the increased speed I'm not sure that you will have any significant added cooling. So increased load beyond rated, inverter operation, no additional cooling... smells like eminent failure to me.
One thing you could try, albeit expensive, would be to boost the line voltage by enough to give you that 3400RPM speed. A motor needs a constant V/hz ratio in order to provide constant torque, your problem as I described earlier is that once you reach full voltage you can no longer keep the V/Hz ratio constant as speed increases. But if you COULD continue to increase the speed and voltage together, you can get more power from the motor. So if you can increase the line to about 3800V, and the VFD and switchgear etc. can take that, then you can program the VFD to provide 3800V at 3400RPM, and the torque will remain constant, the kW output will track and you can run your motor at 3100RPM easily. How you would get there is problematic, but that's a possible route that is likely less expensive than changing the VFD and motor.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: Speed up motor
The voltage increase could be possible, the motor is feeded from one reducer transformer and the output ratio can be increased moving the tap changer, maybe taking a look of the transformer load conditions this voltage rise could be done.
Regards
Carlos
RE: Speed up motor