90deg EMT elbow
90deg EMT elbow
90deg EMT elbow
This question is so simple, I am almost affraid to ask...
A coworker thinks the 90degree conduit elbow bends are no longer allowable by the NEC but I can't find where this is NOT allowable by code.  We have an above ceiling area that is very tight and requires junction boxes every 360degrees.  Could I use the 90deg elbows with removable covers to rest the 4-90degree turns for EMT conduit?
Thanks!
RE: 90deg EMT elbow
NEC 358.6:  EMT, factory elbows, and associated fittings shall be listed.
NEC 358.26:  There shall not be more than four quarter bends (360 degrees total) between pull points, for example, conduit bodies and boxes.
The you're describing is "conduit body."  As long as it's listed for its intended purpose and you don't make any splices in the conduit body, it should be fine by the NEC.
HOWEVER, that's not to say your local jurisdiction has not outlawed them.  It's good to come to eng-tips to get an opinion, but it's much, much, much better to ask the local electrical inspector who will be judging your installation.
Good on ya,
Goober Dave
RE: 90deg EMT elbow
Forgot to mention -- the 2011 NEC has a change, 314.16(C)(3), that prohibits splices and taps within short-radius conduit bodies. (hence my no-splice comment above in previous post).
That may be what your friend heard about.  Check with your local AHJ, though!!
Good on ya,
Goober Dave
RE: 90deg EMT elbow
Be careful of the fill and bending radius requirements unless you use one size larger body than conduit.